Question 1

Can panelboards be installed in clothes closets?

  1. Only in walk-in closets
  2. No
  3. Only with a GFCI
  4. Yes, always
Show the answer

B. No — They also can't be in bathrooms (240.24).

Question 2

What is the minimum working space depth in front of a 120/240-volt panel with exposed live parts on one side and grounded parts on the other (Condition 2)?

  1. 2 feet
  2. 3½ feet
  3. 4 feet
  4. 3 feet
Show the answer

D. 3 feet — Table 110.26(A)(1): at 0–150 V to ground the depth is 3 feet in all three conditions; 3½ and 4 feet apply at 151–600 V.

Question 3

Which entrance requirement applies to large equipment rooms with equipment rated 1,200 A or more and over 6 feet wide?

  1. No entrance required
  2. A ladder only
  3. An entrance at each end of the working space (or other permitted arrangement)
  4. One entrance only
Show the answer

C. An entrance at each end of the working space (or other permitted arrangement) — Doors may need panic hardware (110.26(C)).

Question 4

What is the minimum width of working space in front of electrical equipment?

  1. 30 inches or the width of the equipment, whichever is greater
  2. 24 inches
  3. 36 inches
  4. 48 inches
Show the answer

A. 30 inches or the width of the equipment, whichever is greater — The equipment need not be centred in the space.